การโหลด parameter เข้าเครื่องจักร fanuc controller

เริ่มโดย admin, กุมภาพันธ์ 25, 2018, 05:55:36 AM

« หน้าที่แล้ว - ต่อไป »

admin

To reload parameters
FIRST ! the parameters for 900's do not load on their own, you have to manually input them. Input them from your backup list. If you can't input the 900 numbers then input the 1,2,100,101,102,103,and 552 parameters first.

To load parameters put machine in MDI, emergency stop in and change parameter PWE to 1. this will set alarm, just ignore it and press parameter button again.
First thing to do is load manually parameters number :
ISO = 1
ABS = 1
ALL 900 numbers (ANY 900 NUMBER NOT SHOW IS ALL ZEROS)
900 = 00111001
901 = 01000000
902 = 01000000
904 = 00000001
905 = 00000001
907 = 01000100
908 = 10100000
909 = 01000000
910 = 00001010
911 = 00000100
NOW you can change INCH to 1 (it is located between ISO and ABS) - can't change this until the 900's are inputted. Don't have to do this now but it must be done eventually
0001 = 00000110
0002 = 10000011
0100 = 1 (Command multiplier for X Axes - setting 1=0.5 2=1 4=2 10=5 20=10)
0101 = 1 (Command multiplier for Y Axes - setting 1=0.5 2=1 4=2 10=5 20=10)
0102 = 2 (Command multiplier for Z Axes - setting 1=0.5 2=1 4=2 10=5 20=10)
0103 = 2 (Command multiplier for 4th Axes - setting 1=0.5 2=1 4=2 10=5 20=10)
0552 = 10 (this is the communication bit rate, 1=50 2=100 3=110 4=150 5=200 6=300 7=600 8=1200 9=2400 10=4800 11=9600)
This should make the machine accept the input command to input parameters and diagnostics files with the LSK upload procedure.

Have to take machine OUT OF emergency stop to input rest of parameters with the LSK procedure.
Change machine from MDI to EDIT and press input, LSK should blink in lower right corner of screen. Now upload all Parameters. If LSK doesn't appear, restart controller.
After uploading parameters restart controller and upload diagnostics file WHILE IN DIAGNOSTIC MODE.
After upload, restart machine and check that parameters are correct. Also check diagnostics numbers 300's as these are the timers for the tool changer.
Make sure they are correct also.
IMPORTANT thing to check is parameters
420 Max Tool Capacity
422 is tool in magazine (magazine position)
427 # of tool in spindle
432 is tool in pot. The tool in the spindle should be the empty spot in the tool magazine (no pot).
Make sure (even after uploading parameters) that parameter 0001 is 00000110 , if it isn't you will not be able to MDI any commands into controller.
Also, press OPR ALARM keyboard button twice then the right arrow (KJI) keyboard button to turn Main ABS to ON